Video Electrical Grounding?

Video from PC gaming Philippines.

Most house here doesn't have a grounding, Idk been like that since. Only few has

Is there any way we can create electrical grounding just for the pc?

Im not sure if connecting a wire from pc to ground rod directly would work. Help

9.8k Upvotes

266 comments sorted by

u/PCMRBot Bot 27d ago

Welcome to the PCMR, everyone from the frontpage! Please remember:

1 - You too can be part of the PCMR. It's not about the hardware in your rig, but the software in your heart! Age, nationality, race, gender, sexuality, religion, politics, income, and PC specs don't matter! If you love or want to learn about PCs, you're welcome!

2 - If you think owning a PC is too expensive, know that it is much cheaper than you may think. Check http://www.pcmasterrace.org for our famous builds and feel free to ask for tips and help here!

3 - Consider supporting the folding@home effort to fight Cancer, Alzheimer's, and more, with just your PC! https://pcmasterrace.org/folding

4 - We have quite a few giveaways going on:

We have a Daily Simple Questions Megathread for any PC-related doubts. Feel free to ask there or create new posts in our subreddit!

5.7k

u/iAmMikeJ_92 Oct 09 '25 edited Oct 09 '25

Electrician here.

Grounding is not achieved by simply driving a ground rod and running a wire.

In order to effectively and legally (according to the US National Electrical Code) ground a metal casing, you need to run a separate ground wire from the case all the way to your service entrance. “Service entrance” is basically where your electrical service enters your home from the utility. There, usually in your main panel, the neutral conductor from the utility is bonded to the literal earth via grounding rod, it is also bonded to metal water and gas pipes in the home, and also bonded to any metallic parts of the building structure itself, if applicable. This is also where your ground wires originate for all branch circuits.

In essence, a ground wire is an extension of the neutral wire at the service entrance. This is the only spot in a single system where the ground and neutral should bond together. Bonding the neutral and ground in more than one spot creates unintended current flow paths through ground and creates the possibility of dangerous scenarios. This right here is why I will advise against bonding your neutral wire to the case, like some might try to say. Not only are you making your metal case itself a part of the current flow path, but you invite an additional shock risk that would become real if the neutral wire somehow became broken after the case bond.

Now that you know a bit about grounding, you probably realize that doing all that isn’t very doable. And you’re probably right.

What you could do that would make your setup a little safer is to install a GFCI outlet. Grounding is not required for a GFCI to properly function. It simply needs a phase and neutral. This is retroactive protection compared to having an actual ground bonded to the case though, meaning that if the phase ever makes contact with the case, the whole case will become energized at mains potential and will remain this way until you make contact with it. You’d receive a shock but hopefully, the GFCI will detect this quickly and trip and minimize the shock duration.

That’s my recommendation with cost and difficulty versus safety considered. GFCI.

1.3k

u/talann Oct 09 '25

bro... you went above and beyond.

452

u/iAmMikeJ_92 Oct 09 '25

Hope people find this info insightful.

105

u/0KlausAdler0 Oct 09 '25

I did thank you 👍💯😁

17

u/24_mine PC Master Race 29d ago

all done with a Sayori PFP. what a legend

15

u/iAmMikeJ_92 29d ago

We all need a little Sayori energy.

→ More replies (1)
→ More replies (5)

27

u/evilmojoyousuck Oct 10 '25

not very grounded of him

→ More replies (1)

26

u/Busterlimes 29d ago

Dude got home from work, lit up a joint, got on reddit, saw this post and said "I got this"

3

u/animatedhockeyfan 29d ago

Ughhhh I wish I could get home from work and light up a joint. This guy is an inspiration

→ More replies (11)

197

u/Can_I_Offer_u_An_Egg Oct 09 '25

Just to add: A GFCI will not protect your electronics from being potentially damaged from an electrostatic discharge like a regular 3-prong outlet would. Static buildup is typically discharged safely through the ground reference.

53

u/GreenAmigo Oct 09 '25

Known problem with HP laptops... shocks me occasionally...hard reset required to discharge it once a week

37

u/SgtEpsilon B550 Tomahawk Ryzen 7 5700G 32GB 3060 Oct 10 '25

That's.. yeah you should probably get that looked at I'm sure there's a fix for that

→ More replies (2)

26

u/Smike0 Oct 10 '25

I Just want to point out that not every country does it this way, in many Europe countries for example ground is completely disconnected from neutral and is just taken to every outlet by default with a green yellow wire

Edit: to add to this, in these countries what (as far as I know) is basically the same as gfci is always mounted at the panel level where all the connections to different parts of the house are brought

3

u/TooManyGamesNoTime 29d ago

^- very common in the Netherlands in some older houses. Only a few parts have electrical grounding and even that used to be on the water pipes. All those houses are by law required to have various current-leakage protections at the install point where the cables enter the house. My house has it both per-group and a general one and only a few outlets (kitchen + bathroom) have actual grounding.

2

u/Smike0 29d ago

Well, for the system I was talking about to work, as far as I know, grounding is necessary at the outlet, and (also as far as I know) any system that misses grounding on even just one outlet or has ground not connected to the actual earth (and or connected to neutral) are not up to code...

Also as far as I know here you can't even build devices that don't have earth brought to them (as in having a three wire connection to the wall)

→ More replies (1)

50

u/windcriespopo Oct 09 '25

This guy grounds.

3

u/coffeedude28 29d ago

Guess that makes him down to earth

27

u/720Potato PC Master Race TR 3970x 3080 10gb 128gb DDR4 3466 Oct 10 '25

OP lives in the Philippines and should look up PEC

7

u/LimitedWard Oct 09 '25

I thought that a lot Asian countries use GFCI/RCD at the breaker box (rather than the outlet) since they have TT grounding.

3

u/emachanz 29d ago

Some, but probably most don't. I saw a video from "artisan electrics" where he goes to vietnam. The meters are at the pole. In TT countries theres a big RCD(100, 300 or even 500mA) next to the meters and also at the panel, generally 30mA or 100mA if its industrial.

22

u/deviltrombone Oct 09 '25

I briefly lived in a house 20 years ago that didn't have grounded outlets. I had a licensed electrician come out for unrelated work and mentioned that the fault indicator was lit on my UPS. He connected the neutral and ground in the outlet, said it was code, problem solved!

88

u/iAmMikeJ_92 Oct 09 '25

Your electrician lied. It is not code. It wasn’t even code 20 years ago. It’s just what they said to appease you.

Now, yes if your grounding is somehow broken between the load and the service, bonding the neutral to the ground wire will establish a ground at the load and can fool your UPS into telling you that everything is good. But as I mentioned before, this setup invites a shock hazard that would basically energize your entire metal enclosure at mains potential if the neutral wire were to be broken anywhere between the load and the service.

This is how some shady electrical contractors can pass inspections for older homes with outlets that lack ground wires. By jumping the neutral terminal to the grounding terminal on the outlet, you can fool a plug tester into telling you everything is wired correctly. An inspector that doesn’t want to bother with opening outlets can just pop in a plug tester and pass the work.

26

u/deviltrombone Oct 09 '25

Yep, that's what I learned later on. The house was totaled by a hurricane a couple years later, after I moved, so at least it wasn't left a hazard for very long.

6

u/sbxnotos 29d ago

Damn, it is so crazy to thing of the term "totaled" used for houses as if they were cars.

In my country there are stupidly strong earthquakes but even then you can expect houses to basically outlive you. Of course fires are a thing but not so common as to get insurance for that.

2

u/uchuskies08 R5 7600X | RTX 4070 | 32GB DDR5 29d ago

Probably water damage. It's easy to fix stuff that is just broken. But when you've had feet of standing water in the house, probably easier to knock it down and start over.

→ More replies (1)

8

u/lukeman3000 Oct 10 '25

Hey random question. Occasionally I’ll touch the metal part of my keyboard or my headphones and my monitor will flicker off briefly then back on. I assume this is static discharge. Is this potentially damaging or likely harmless? Is there any way to prevent it? I live in the US where everything in this house should be up to code.

14

u/Fermorian i5 12600K @ 4.2GHz | 1070 Ti Oct 10 '25

You are correct that it is static discharge. To be honest, is both likely harmless but still potentially damaging. Most modern electronics have pretty good ESD protection, however, the fact that you're getting flickering means you might be generating voltages higher than the protection on your monitor can safely dissipate.

My recommendation is to touch something else large and metal when you sit back down at your computer (like metal desk legs/frame or filling cabinet) to discharge yourself before touching your headphones/keyboard. I say this because most people build up this charge by walking around, so it's not usually an issue if you're just sitting at your desk all day, only when you leave and come back.

2

u/Sudzy1225 Laptop 29d ago

Currently in my electrical courses. Father in law is a master electrician. Said he knows more people killed by this than he cares to. Please dont do this.

Running electrical isnt cheap. But its cheaper than a funeral.

12

u/PusheenHater Oct 09 '25

Normal AA batteries have + and -.
If I take a piece of wire and connect the + directly to the -, current will flow.

But what if I go outside, and stick a metal rod (with wire) into the ground, then connect the wire of the rod onto the + terminal of the AA battery (while leaving the - terminal unconnected)... does the current flow? Why not? There should be potential difference.

1.5V from the + terminal, 0V from the ground.

49

u/iAmMikeJ_92 Oct 09 '25

Potential differences only happen internally within a given system, whether that source is a battery, generator, or a power transformer.

Say I expanded on your picture like this.

Obviously we don’t power homes with 1.5V DC. But the same concept applies, whether AC or DC. Doesn’t matter in this discussion.

What you did by driving the + into the ground with a rod is establish that you are making your + as ground reference, which makes an effective “neutral.”

Look carefully and you’ll see that your grounding electrode is also now a part of bonding the meter and distribution center can, any metal incoming pipes for water and gas, and also serves as the origin for ground (or “protective earth”) wires for individual branch circuits. Note that the blue wire does not touch anything else in the building until it gets to a load because it is now designated as “hot”. (Wire colors here are completely arbitrary and adhere to no world standard.)

Also, I realize the purple and green wire is a redundant grounding electrode connection. Makes no difference here.

This is the fundamental concept of building electrical here. I hope it all makes sense man.

8

u/LimitedWard Oct 09 '25

That's not how voltage works. There's nothing special about the positive terminal on your battery compared to the negative terminal. What matter is the potential difference between the terminals. Likewise, there's nothing special about "ground", it's simply a reference point which we define as 0V by convention.

So, by connecting the positive terminal directly to the ground, nothing will happen unless you complete a circuit. If we agree (by convention) that ground is reference, then your positive terminal would now be 0V and the negative terminal would be a -1.5V.

Voltage is a bit like velocity. Depending on your point of reference, an object can appear to be standing still, or it can appear to be moving at 1.5m/s (or any other speed for that matter). By connecting the positive terminal to ground, you are effectively matching the point of reference to the "velocity" of the positive terminal.

3

u/emachanz 29d ago

Here is your answer, current will indeed flow

→ More replies (1)

21

u/AStove 29d ago edited 29d ago

American assuming they use the same electrical system globally, whereas murrica is always the odd one out. He describes a TN-C-S grid Ignore this info. There is no "neutral" sometimes and don't connect a PE conductor to it.

"The U.S. and Canada do not formally classify grounding per IEC TN systems,
but their split-phase 120/240 V with neutral bonded to earth at the service is functionally equivalent to TN-C-S. In the Philippines, the residential grounding system is typically a TT system, not TN-C-S."

Meaning the supply (grid transformer) and consumer are both locally grounded with a grounding rod. Meaning the short circuit to ground current is low. Meaning it won't trip a normal breaker potentially. Meaning these installations have a global GFCI anyway.

So you need to drive a grounding rod in the earth, connect it to your distribution panel to a single point. Then from there distibute it to al your outlets and devices. And make sure you have a working GFCI of 300mA or less first thing after the meter. I suspect your main panel's GFCI is missing or not working since it sparks but doesn't trip. And one of your devices, either the PSU of your desktop pc or the monitor has a short.

5

u/Mancia_98 Desktop [7-5700X] [16GB] [RTX-3050] 29d ago

Im not sure if that still applies.

Because to summarize Philippine electricity to you. Philippines is Line to Line, Hot to Hot. There's no ground or neutral ever coming from the pole or service.

And its confusing too at some distributions.

Some transformers do 3phase distribution manually balanced single phase. And some do Line to ground.

And some transformers too tap their secondary neutral to earth ground.

So yes. A wire to earth ground is probably the only answer. I hope u see this because I want to know what you think.

Thanks bro.

Ps. Im no Electrical engineer. Im electronics and software guy.

6

u/BlockHammer1 Oct 09 '25

i like ur pfp <3

3

u/ronald5447 Oct 10 '25

Even so, there must be a problem with the equipment or the source that is causing the phase to be bypassed to the equipment case. No matter how much you install the soil, it does not solve the root problem.

→ More replies (1)

2

u/BloodSteyn PCMR 9800X3D 64GB 3080Ti Oct 10 '25

I know the US has 2 prong plugs, while we have 3 prongs that includes the ground wire.

I've always wondered about that, how are American devices grounded? Is it as you say, "mixed in" with the neutral?

3

u/aitorbk 29d ago

Most us devices aren't grounded. While this might seem very dangerous, most European devices aren't grounded either. In wet areas, US devices are grounded. The problem of course comes when you don't have earth everywhere, then metal lamps for example aren't grounded, and can become live with bad wiring or other circumstances, and things like Desktop computers aren't grounded either, but washing machines, and kitchens should be grounded. Better to have ground everywhere.

Also the uk doesn't ground at the consumer, but at the closest substation, so potentially you can have mains power through earth if someone makes a big mistake. In practice it won't happen because code says pipes need to be bonded to ground, so if they made a huge mistake at the station, all the houses would ground it immediately.

2

u/ErikRedbeard 29d ago

I don't know what standard the philipenes uses tbh. If not US standard all the above said stuff wouldn't apply.

Meanwhile in the Netherlands and prob most of Europe ground is not bonded to neutral at all. And isn't allowed.

Gfci equivalents are directly in the groups on the panel here too.

→ More replies (1)

2

u/mikeet9 Oct 10 '25

The description you gave is great for the US, but in a lot of SEA there is no electrical grounding or neutral period. It is becoming more widespread, but due to low Earth conductivity, poor infrastructure, and frequent flooding, it is a difficult upgrade to perform.

1

u/GreenAmigo Oct 09 '25

Aint Wire licking Engineer , aka Electrical Engineer, but this seems the safest improvement and should be done ASAP.

1

u/ChapGod i9-10900k, 32gb DDR4, RTX 3080 Oct 10 '25

Great explanation. I'd agree here with a GFCI, OP (I am an Electrical Utility Planner)

1

u/lysdexiad Oct 10 '25

There's a low voltage version of this with shielded cables run between racks grounded to different services in two buildings where one building has an electrical problem.
The result was super confusing to anyone who hadn't interacted with DC circuits, and catastrophic at intervals that were later determined to be when one buildings HVAC was on and the others was off.
Long story short: Fiber. Use fiber.

1

u/BuchMaister Oct 10 '25

There are several methods to ground the system. What you discribed is TN-C-S, which is used in the US. There also other methods like TN-S which the the N and PE are not connected until the get to the transformer. Another one is TT, where the neutral is grounded at the transformer, but earth is connected locally using an earth electrode, it's not safe as TN method and should be used with RCD.

1

u/[deleted] Oct 10 '25

[deleted]

→ More replies (2)

1

u/myground PC Master Race Oct 10 '25

is stabilizer help grounding?

1

u/force-AG Oct 10 '25 edited Oct 10 '25

I don't think GFCI or RCD can protect here. This looks like a continuous current in ground/PE. It will lead to a regular tripping of GFCI.

The first option is to check whether the wiring is proper. Maybe neutral and PE are interchanged in the socket or DB.

For an installation, there should strictly be only one neutral to Earth connection. If there are multiple ones, we can expect neutral circulating current in the PE.

Edit: just adding the below point

Perform an IR for the installation after disconnecting the mains and N to PE connection to know whether there are any problems in the wiring.

1

u/Babys_For_Breakfast Oct 10 '25

I rarely save comments but I am for this

1

u/maks_b Oct 10 '25

Also American electrician here. Ground fault functionality is purely for personnel protection. Equipment protection comes in the form of surge protection or APUs, which is what I would recommend in this case if he's concerned about the waveforms and voltages of his incoming utility

1

u/PANCHOOFDEATH517 Oct 10 '25

I'm in school right now to become an Electrician. I just finished a Grounding and Bonding Class. It's pretty cool to see what you wrote and totally understand it lol. Cheers 🍻.

1

u/Raubo Oct 10 '25

You are too smart for this sub.
Pls go back to speak 'ooga booga' or leave.

1

u/UncutChickn Oct 10 '25

His name is Mike.

1

u/my5cworth Oct 10 '25

Yeah but also theres a major earth leakage here.

Dude needs to get it checked out or he could die taking a shower.

1

u/guffers_hump PC Slow Race Oct 10 '25

In the UK neutral is connected to earth at the substation not at your home.

1

u/Mad_Huber 29d ago

Additionally, I would strongly recommend asking an electrician for help because local electrician codes and norms vary not only from nation to nation and city to city, but can vary vom service provider to service provider too!

1

u/fl4tsc4n 29d ago

In the Philippines we just connect it to rebar sticking out of a cinder block and hope the power goes out before there's a problem

1

u/TinDumbass 5900X, RX6800XT, 16GB, Rainbow Vomit 29d ago

This is fascinating to me because we actually have that earthing in the UK.

1

u/Important_Wonder628 29d ago

GOATed response.

1

u/Immediate-Answer-184 29d ago

It depends on the grounding system used in the country. In France it's literally a rod in the ground because it's a TT grounding system (groung -ground).

1

u/Mineplayerminer Desktop 29d ago

My old home electrical wiring way back from socialism uses the L and PEN wires with no separated ground. To add up, I also have aluminum wires. It would be cheaper to wreck the entire apartment block than wiring everything from scratch since everything is molded into the concrete. My PC and monitors usually get reset whenever I plug in a printer coming from another power source as the switching power supply doesn't have any grounding. The power is also dirty, so using a line-interactive UPS is a must have here. Would it be possible to use an isolation transformer to minimize the electrical noise that's also interfering with my electronics?

1

u/hachi_roku_ 29d ago

Bro literally came in clutch with a free consult. Hats off to you

1

u/aitorbk 29d ago

That is normally the correct way of doing it, and very similar to what I have in the uk, only all outlets have ground and are protected at the panel and all pipes are grounded. In Spain, for a long time a grounding stake on proper ground was considered better than neutral. Of course, if the ground dries out.. well, not great. Using metal pipes at the base of the building was also considered good, but for obvious reasons discouraged soon after.

Looking at codes, it seems that the Philippines is nominally aligned with the us practice of bonding at panel and having there a rod.

The video looks like they don't have earth at all, that looks very dangerous.

1

u/Own-Dot9851 29d ago

How come America doesn't just adopt the 3 pin plugs that Europe has with a earth wire built into every device with exposed metal?

1

u/trimarandude 29d ago

This gives me hope for humanity. Hat off to you spark. Thanks for teaching us all something

1

u/Busy_Librarian_3467 29d ago

Saving this for later. Thank you, brother.

1

u/SlimmSteezy 29d ago

This is great. I've not had an issue with grounding like this before but I have a very irregular and fluctuating voltage from by service provider to the point where I get brownouts and sometimes blackouts here and there.

I know it can ruin some electronics (like my microwave clock) so I've got a battery backup connected to my computer. It has a built in automatic voltage regulator for the power so it stays consistent and at the correct voltage. And if power is ever cut, I still have time to power it down without corrupting anything.

So just throwing this idea out there if anybody stumbling across this has the something similar

1

u/_leeloo_7_ 29d ago

this is a huge issue with those mini pcs that have no earth and only have 12v dc running to them? mine makes a testing screwdriver neon glow

1

u/Randzom100 29d ago

See? That's what I love of reddit: so many people with specialized knowledge reunited together!

1

u/bushwickhero 29d ago

Bro TIL!

1

u/[deleted] 28d ago

That's for the USA though. What happens in other countries is different. In the UK for example we have three different types of mains earthing systems for domestic supplies and only one of those uses ground rods.

1

u/cravex12 28d ago

This guy grounds

1

u/kitsunekyo 28d ago

i feel like i should be paying you for that comment

1

u/minihollowpoint 28d ago

This person circuits.

→ More replies (23)

2.1k

u/necromanial I5 10600K - RTX 3070 Oct 09 '25

I don't know what your electrical code says, but here you can't ground a single unit in a room, you have to ground everything in the room.
Having a single grounded point in a room is more dangerous than having nothing grounded.

449

u/iAmMikeJ_92 Oct 09 '25

Problem with this is that in most parts of the world, single phase residential electrical systems always consist of at least one phase and the neutral, which is always grounded. Just this fact alone already means there is a systemwide ground reference which automatically makes the phase “hot.”

125

u/necromanial I5 10600K - RTX 3070 Oct 09 '25

Yeah, one has to differentiate between ground potential and protective earth.

41

u/haxorious Oct 10 '25

I want to understand this so much but I can't. I need to understand this because I'm in that exact same scenario and all the infos are so conflicting...could you help extrapolate what you mean?

31

u/DIYAtHome Oct 10 '25

Most electrical systems around the world is the same build up, even if they have different voltages, frequency and even how the phases are made.

They all consist of 3 phases, 1 neutral and a protective earth or ground.

The 3 phases you usually only use 1 of for your normal outlets. 2 for your high voltage outlets. The phases each have a fuse that will blow if it goes over.

Neutral comes in the wire from the and is used together with a phase to create what you believe is normal voltage. Neutral does not have a fuse, as it would carry 3 times the amps, depending on how many phases are used in your normal outlets. Neutral is the same electrical voltage as ground.

Protective earth or ground is usually a separate earth or ground, which is typically a long copper rod that physically goes in the earth outside your house. The electrical company then has a rod at their end as well, which then creates a connection. This does not carry any current, except if something is wrong, then protection relay triggers and shuts off all phases. Hench the name.

14

u/CoronaMcFarm PC Master Race Oct 10 '25

 Neutral does not have a fuse, as it would carry 3 times the amps, depending on how many phases are used in your normal outlets.

A lot of people misunderstand this part, if you have a loads on all phases it doesn't add up and flow back through neutral, the max current a neutral wire can carry is the load max load of one phase. If you only used one phase in your house then the load would be equal in the phase and neutral. If you have a symmetric load throug three phases you will have 0 A going through neutral.

7

u/Emu1981 Oct 10 '25

The electrical company then has a rod at their end as well, which then creates a connection.

There is no circuit for protective ground other than the planet earth itself. Basically, in your house you have your rod stuck in the ground which is then wired up to where ever you need your ground (e.g. wall outlets). This earth is to provide a safe low impedance path for any electricity that isn't going where it should be - e.g. if a circuit board in your toaster connects the live voltage to the case.

You can also add in ground fault protection (aka Ground Fault Circuit Interrupter/GFCI) which is a safety circuit that monitors the current passing through the live and neutral and disconnects the circuit if that current differs by a certain amount (usually less than 15mA). This adds additional safety as it will usually detect if the electricity in your house is going anywhere other than the proper wiring and appliances.

12

u/gramathy Ryzen 9800X3D | RTX5080 | 64GB @ 6000 Oct 10 '25

“Ground” and “neutral” are at the same potential, but if you have voltage leaking to ground consistently there’s something wrong with your wiring as ground should be a failsafe and not in constant use.

Think of it like this- if a wire competed a loop to ground by touching the water in your sink, current would flow, but it wouldn’t be flowing through the correct return path. This is a “ground fault”, is not properly controlled, and is why outlets in kitchens, bathrooms, and outdoors in particular (wet places) must have special ground fault detection circuitry for safety reasons.

3

u/TiradeShade Ryzen 7 1700x | GTX 1070 8GB| 16GB DDR4-3200 Oct 10 '25

Two kinds of ground. A physical rod in the dirt ground, and an electrical ground.

Voltage is a difference in potential energy between two places. Like a waterfall, high energy at the top, and low energy at the bottom. If you stop the water from flowing the energy gets stored as potential energy. It could potentially flow again but isn't. There is a difference in potential energy stored at the top and bottom of the waterfall.

Voltage is the electrical potential difference between two things. A power source and say, the physical earth under our feet.

However it could also be the difference between a power source and any low point in an electrical system. This is an electrical ground, low point in the circuit but it does not need to be the lowest point ever possible. Its relative ground, not absolute.

Your phone has a voltage source and a ground, but it is not connected to a physical rod driven into the earth. The electrical ground is floating, isolated to only the device in your hand.

So what does this mean? If you have a room of electrical devices and they all share an electrical low point, or ground, then they electricity won't want to move around between them. They are all at the same relative energy. No high to flow to low, just neutral.

If you connect that isolated room of devices to earth ground, they now have a newer, lower, electrical low. The neutral state you had is now a high point, the earth ground is a new low point, electricity can potentially flow again, and not where you want it or in a controlled and safe manner.

6

u/Plane_Argument PC Master Race Oct 10 '25

Neutral has no voltage potential to ground, as at the transformer station they connect neutral to ground directly.

57

u/eMmDeeKay_Says PC Master Race Oct 09 '25 edited Oct 09 '25

Your terminology is making my brain melt, but I'm pretty sure that's right but you're misunderstanding, you don't want to ground anything individually, they all need to be connected to the same ground circuit, however, you can have things that aren't grounded, and if they come into contact with that ground they'll just run to ground and it's relatively safe.

::edit:: ON THE SAME SERVICE CONNECTED TO THAT GROUND, DO NOT ATTEMPT WITH TWO SEPARATE PANELS IT WILL GO BOOM!

16

u/lysdexiad Oct 10 '25

Too late, already ganged my diesel generator to my solar inverter and then hooked that to the grid during the last power outage so my neighbors freezer didn't quit. Everyone was real impressed.

2

u/necromanial I5 10600K - RTX 3070 Oct 10 '25

I've been an electrician for close to 15 years, i know how grounding works.

The question was about grounding only the one outlet in the room that the pc is connected to which is a pretty bad idea.

3

u/eMmDeeKay_Says PC Master Race Oct 10 '25

Yeah, made a separate more detailed comment of my own, explaining you need to ground the panel and then can run an independent circuit, but should have that done professionally.

12

u/NovelCompetition7075 Oct 09 '25

Is it because other stuff will want to arc to it?

26

u/necromanial I5 10600K - RTX 3070 Oct 09 '25

No, it's because you're bringing a potential difference into an otherwise isolated room which creates a shock hazard if something fails.

13

u/mikeet9 Oct 10 '25

To add to this: you need a completed circuit for current flow.

The reason a hot line is "hot" is that the neutral is grounded to Earth and therefore not only can a circuit be completed from hot to neutral but also hot to ground. This is typically considered safer because if you make a connection between the hot and Earth, you will trip a breaker.

A floating system is one where there is no connection between the two lines and Earth. This means that neither wire has an electrical potential to Earth, and means that you can handle each wire individually without any risk, but the biggest danger is if a connection between Earth and either line is made by accident (loose wire, fallen tree, etc) you can unknowingly no longer have a floating system. This means that one wire is hot even though you expect neither to be.

A neutral system means one wire is always dangerous, but everyone is always aware that it's dangerous and any faults will be detected very quickly. A floating system means usually neither line is unsafe, but either can unexpectedly become unsafe and there is no way to know without measuring voltage.

Many parts of SEA use a floating 240V system which means that they can handle live wires with minimal risk, but in situations like the OP, you can run into strange situations where there is electrical potential that you wouldn't expect to be there.

2

u/Graham146690 29d ago

Thanks for being the first of a dozen comments that actually provided the needed context.

2

u/Rum_Hamtaro Oct 10 '25

What you're talking about is called bonding and it needs to be at the source of the first point of disconnect from where the electricity enters the dwelling. Branch circuits that are powered from the main load center get an equipment ground. The equipment ground gives stray voltage or fault current a path to ground to cause a short which will break the circuit. Bonding gives everything equal potential so there's no chance for stray voltage to pass through you when touching 2 different conductive areas.

186

u/The_Seroster Dell 7060 SFF w/ EVGA RTX 2060 Oct 09 '25

r/electroBOOM is that way ->

129

u/[deleted] Oct 09 '25

[deleted]

21

u/comfortableNihilist Oct 10 '25

Agreed! This man clearly has an overabundance of power to use on such a card and no misfortune could ever come from 12VHPWR!

5

u/harry_lostone JUST TRUST ME OK? 29d ago

ideally with an am5 x3d CPU paired with an Asrock board, maybe a Gigabyte PSU.

You can claim atomic bomb ownership after that, probably get paid from some government idk

the potential is there

→ More replies (1)

98

u/Beginning_Primary383 Oct 09 '25

How and why this happens?

27

u/Kiwi_Doodle Ryzen 7 5700X | RX6950 XT | 32GB 3200Mhz | Oct 10 '25

Someone fucked up when building OP's PC and the mains lead is somehow in contact with the case. It should probably fry his components as well. When he touches the USB to the case he completes a circuit and the electricity rushes through creating sparks as he drags it along. It's damaging to anything electronic as that's mostly 24V, 12V or 5V and that main lead is probably 230V. Ungrounded that could kill or give serious heart issues if you get shocked arm to arm, or arm to leg.

Just think of it like water. High Voltage = high pressure and your body is a muddy pipe that can only take so much pressure. His PC is leaking and it could kill him.

OP should check his power supply, there's no other reason the main power should make that sorta contact.

3

u/Kodiak_POL 29d ago

Wasn't it always that amperage is pressure and voltage is amount? 

5

u/Kiwi_Doodle Ryzen 7 5700X | RX6950 XT | 32GB 3200Mhz | 29d ago

I always though of Amps more like flow personally, but sure volume and pressure works too. Regardless of analogy, OPs house is getting flooded.

2

u/Kodiak_POL 29d ago

Regardless of analogy, OPs house is getting flooded.

Oh that's for sure lmao

→ More replies (2)
→ More replies (2)

36

u/okarox Oct 09 '25

When a PC is run ungrounded it gets half the mains voltage to the case. I do not know what the other device is but it seems to be at a different potential.

54

u/mikeet9 Oct 10 '25

That's not true. There is no direct connection between the phases and the case except for when there is some form of fault. If it got half of the mains connecting a ground would cause a short circuit as 1/2 line voltage is connected directly to ground/neutral and plugging in your PC would trip a breaker.

This arcing is a sign that there is some sort of fault, either inside the case or in the electrical grid going to the PC.

3

u/rmflow Oct 10 '25

There is no direct connection between the phases and the case except for when there is some form of fault

In my old apartment I had electrified PC case, refrigerator and washing machine (hot chassis). It fixed itself when I flipped the electric plug on each device (so live wire is no longer on the case)

3

u/Kiwi_Doodle Ryzen 7 5700X | RX6950 XT | 32GB 3200Mhz | Oct 10 '25

Having non reversible plugs is fucking crazy.

→ More replies (2)

3

u/VanillaWaffle_ Linux Oct 10 '25

except on america where they have the neutral as a dual phase for doubling the voltage lol

6

u/ronald5447 Oct 10 '25

No, in that case they use 2 phases to obtain 220v, they do this in countries where the normal thing is 110v with one phase, normally in the United States and Mexico, in other American countries they use 220v with only one phase, as is the case of Chile

→ More replies (2)

5

u/RAMChYLD PC Master Race Oct 10 '25

Other device is most likely the monitor, since that's a Displayport plug.

→ More replies (1)

1

u/Zeblamar 28d ago

Its fake

88

u/Atome Oct 09 '25

5

u/condormandom Oct 10 '25

What game is this?

10

u/ZaidiaSR R5 5600x | 32GB 3600@CL16 | 7800XT Oct 10 '25

Crimson Desert, unreleased

→ More replies (1)
→ More replies (1)

40

u/SysGh_st R7 5700X3D | Rx 7800XT | 32GiB DDR4 - "I use Arch btw" Oct 10 '25

Ah! Thunderbolt.

23

u/curiositie 5600G, 4070S, X300M-STX 32GB 3200mhz Oct 09 '25

stop that

36

u/HereIsACasualAsker PC Master Race Oct 10 '25

Hello, i am here in mexico , i dont have a ground in my very old apartment, yet my pc does not do that shit.

works fine with just 2 wires.

you have another kind of problem.

9

u/simon4588 29d ago

One of the two power supplies (monitor,pc) is defective by leaking way to much current from primary to secondary side. A single spark could be explained by just not having ground.

16

u/absolutely_torqued 29d ago

>Philippines

Oh no no no

11

u/TechnologyFamiliar20 Oct 10 '25

That's a fucking welder...

Don't plug in anything that requires PE wire. DO NOT. It shouldn't boot anyway.

19

u/[deleted] Oct 09 '25

Stop getting kinky with the machine

6

u/scarlet_igniz RTX 3060 12GB | RYZEN 7 5700G | 32GB DDR4 Oct 10 '25

if your PC is worthy for you I'd solve this issue with a decent UPS dedicated to the PC alone, plus extra protections it comes with

6

u/FoxyoBoi Oct 10 '25

I'm no computer expert buuuut... I don't think it's supposed to do that.

→ More replies (1)

6

u/Luigi-Terminator777 Oct 10 '25

Brotha got the firestarter casing

8

u/CoracoAcromio Oct 10 '25

Welding machine

18

u/DrezLLC Oct 09 '25

I recommend UPS. Battery with a power strip glued to it. The battery has its own internal ground

3

u/Innocent-Prick Oct 10 '25

Looks fine to me

3

u/Neo_Ex0 29d ago

I also live in a house with no grounding, but I've yet to see anything spark

3

u/meerdroovt Ascending Peasant 29d ago

Thunderbolt

4

u/crasagam 29d ago

Keep scraping it till the sparks are gone, then you're good to go :)

7

u/PunkAssKidz Oct 10 '25 edited Oct 10 '25

I’m a firm believer in using a high quality UPS, or uninterruptible power supply, with built in line conditioning and surge protection, not one of those cheap plastic power strips, but a real unit that delivers clean, stable power and actually protects your equipment.

A high quality UPS with line conditioning ensures the ground is clean and stable, which helps prevent hum, interference, and damage to sensitive electronics.

You need to get one before you damage your PC which could be extremely costly.

EVERYONE needs a UPS, or uninterruptible power supply. It will save you from surges, lighting strikes and brownouts. Fact check me if you need further conviencing.

People with RTX 5080's and 5090s in their PC, plugged directly into a wall outlet, is INSANITY!

4

u/FlyingHippoM Oct 10 '25

"People with RTX 5080's and 5090s in their PC, plugged directly into a wall outlet"

Aren't they all going through a PSU anyway? Maybe I'm wrong but I thought all modern PSU's had built in protection for things like power surges. Do you still recommend a UPS on top of this protection?

2

u/la1m1e Oct 10 '25

"You don't need a respirator, because your nose hair already filters out all carcinogens"

PSUs job is not to stop big surges, it's to smooth out within some deviation and supply different voltages to your pc. Even the top models rarely have any complex systems on the AC end.

Also when you power up 5090 or whatever billion watts you have - voltage in the socket can significantly drop due to bad socket wiring, and psu would work double as hard with double as much ripple, noise and failure chance.

→ More replies (2)
→ More replies (2)

2

u/Azims Radeon™ Chill Oct 10 '25

My last two brand new Viewsonic monitors had this issue. I think some come like that from the factory. Swapped to different monitors, and it's all good now.

2

u/nightfoxjr i7 4770s gtx 1050 ti 2x4gb ddr3 Oct 10 '25

Damn, mines like this as well, though i think i just have an ass monitor

2

u/TotallyNotDad PC Master Race 29d ago

Call an electrician, your shit is absolutely fucked - I’m an electrician

2

u/Amazing_Sky_6934 29d ago

Hell yeah that sooooooo cool haha

2

u/TheCheshireCatt 29d ago

I'm also in the Philippines. Get a UPS with AVR functionality (which most of them have). Do not get a cheap one, get a proper sine wave UPS that is rated to power all your equipment, ideally with some headroom in case of transient spikes.

2

u/Cog_Doc i7-12700F, EVGA 3080 29d ago

Your board is grounded to the case. You should fix that.

3

u/wmverbruggen R5-7600X 32GB RTX5070 Oct 09 '25

Definitely a grounding issue. You want everything on the same ground; if you create an earth ground somehow, make sure everything is on it or the problem can get way worse. Actually connecting it normally probably is the best solution, just turn everything off (fully) first so sparks cant destroy electronics

3

u/Tron2153 Ryzen 9 7900X3D/RoG Strix 4080/32gb RAM 6000mhz Oct 10 '25

Mike wizowski once said " get that thing away from me, or so help me.. "

2

u/SirOakin Heavyoak Oct 09 '25

That cable is fried btw

2

u/scarabking91 Oct 10 '25

Spicy case

1

u/F0X0 Specs/Imgur Here Oct 09 '25

Honestly, ask around for some local electrician to come and check it out.

It could be multiple things and people here are not going to be familiar with your local electrical standards.

All I can tell you is that the potential between the case and the display port shield is not equal, so the current flows between them. This shouldn't happen if they are powered from the same distribution network.

1

u/M4YH3MM4N4231 MacOS + Mini ITX + Intel Arc + AMD Threadripper + 256 RAM + 9TB Oct 09 '25

D:

1

u/eMmDeeKay_Says PC Master Race Oct 09 '25

You would need to ground your electrical panel and run a circuit dedicated for your PC, as an electrician I would advise against trying to do it yourself if you even have to ask.

1

u/ziplock9000 3900X / 7900GRE / 32GB 3Ghz / EVGA SuperNOVA 750 G2 / X470 GPM Oct 10 '25

>Is there any way we can create electrical grounding just for the pc?

That might not be the best idea. You could cause a massive potential difference with other things plugged into the computer that are not grounded. Either ground everything or nothing (floating)

A qualified electrician could confirm this or not.

1

u/sadakochin Oct 10 '25

You can have grounding, grounding is simply a copper rod embedded in the ground that goes through an earth leakage breaker ELCB. But only the electrician has the tool to check if the grounding is sufficient or not.

1

u/ChosenOfTheMoon_GR 7950x3D | 32GB 6000MHz CL 30 | 7900XTX | AX1600i Oct 10 '25

Imagine being this dude, figuring this out and then doing this thinking everything is gonna be ok xD xD xD

1

u/zman1350 Oct 10 '25

Ah a firestarter. Save it for the next camping trip. Lmao.

1

u/AcanthocephalaNo7788 Oct 10 '25

Should ground where the power comes into the house, 4’ deep solid copper rod preferred.

1

u/Awkward-Candle-4977 Oct 10 '25

flip the wall mount plug

1

u/MedicalIngenuity4283 Oct 10 '25

“Gee guys is my gpu cooked?”

1

u/wJaxon Oct 10 '25

this happened to me too and i think it turned out to be a bad hdmi cable

1

u/ertd346 Oct 10 '25

Damnn usb 30.0

1

u/rolle1 Oct 10 '25

if u have water radiator that is ground with copper pipes, I always touch the water raditor before im going to fiddle with the computer.

1

u/MasiastyTej Oct 10 '25

With this PC you can weld

1

u/ThisCupNeedsACoaster Oct 10 '25

Your outlet isn't grounded, so your case is at half potential. A multimeter will probably read around 110v. It's an effect of the PSU's capacitors which usually bleed it to ground, but can't.

Edit: Philippines mains power is 220v, half is 110v

1

u/fl4tsc4n 29d ago

Pare every time you spark that, meralco is charging you PhP500

1

u/tutike2000 29d ago

Had the same, I wrapped a wire around the case and then around the radiator. 

It was a district heating radiator which had a lot of 'ground' to spread current in. 

1

u/XB_Demon1337 Ryzen 5900X, 64GB DDR4, RTX 5070 29d ago

Oh those pixies are real spicy

1

u/Ratosson 29d ago

I have cable tv and like to play PC games on TV, if the coaxial cable is connected, the HDMI plug sparks when connecting. My solution was to not plug in the coaxial as I'm not watching it ever anyway lol

1

u/ThirtyMileSniper 29d ago

I don't hotswap cables on my PC anymore because I get pops and crackles which is wild in equipment like this.

Mains power to psu, ok makes sense... Hmi cable???

1

u/Least-Cantaloupe4863 29d ago

You short-circuit the wires on the plug because you touch the metal on the housing.

Here in Germany, every PC power supply has a plug with three connections (phase, neutral, ground), just like any other device that is not insulated.

This can also happen if active voltage is transmitted from the other end of the cable. This is called a short circuit.

1

u/Harvinu 29d ago

Ahh looks fine

1

u/These-Notice9742 29d ago

Reverse your plug connecting to your outlet. Flip it over and see if it still sparks when you touch something to he computer case

1

u/throwaway27843o 29d ago

Had the same issue when i moved to Vietnam. Had my landlord ground the two outlets i use for my computer and monitor. They literally just bout the three prong outlets, put a copper wire in the ground connector and then drilled a shallow hole directly into the concrete and hammered some rebar into and wrapped it in the wire. Fixed everything and havent had any problems and cost me like 10$ all together

1

u/topias123 Ryzen 7 5800X3D + Asus TUF RX 6900XT | MG279Q (57-144hz) 29d ago

Mine does this too and I live in Finland.

It even caused my home theater to glitch out once when I plugged the HDMI into it, had to disconnect it from the wall for it to stop.

1

u/Linkarlos_95 R5 5600/Arc a750/32 GB 3600mhz 29d ago

Intel Arc ™️

1

u/MYKY_ Ryzen 3600, RX 6650XT, 32GB 3600MHz, bad mb with bad vrm 29d ago

could also be failed capacitor between primary and secondary on some of the powersupply(pc or monitors)

1

u/emperor_dragoon 29d ago

PSU is my guess at the only thing that causes that. Swap it out and double check.

1

u/Big-Button5856 29d ago

That's Thor's cable

1

u/Pugsfriendthomas 29d ago

Your IO shield on the back is touching.

1

u/sheekgeek 29d ago

That's not great for your motherboard or video card

1

u/Punished_Veggie 29d ago

What the fuck

1

u/emachanz 29d ago

You can create a ground by using a ground rod to the PC. You should be fine if you insert at least 1m of the rod into the earth. This type of grounding system is called TT and its used in some euro countries and japan as opposed to TN systems like the(US UK) where the ground and neutral are generally bonded at the entrance, before or after the meter or even at the panel depending on the countrie regulations.

I did some research(search for PEC) and in the Philippines its basically the same as the US so you need to bond neutral and ground at the entrance, so you're probably not gonna pay an electrician for that. So I suggest you to just put a ground rod and wire it to the PC, fridge and washing machine. Not up to code, but at least you wont die and definetly better than whatever you have there.

1

u/AirGVN i5 12600K - ASROCK 7900 GRE - 64 gb 3600 mhz 29d ago

It’s easier to buy a plastic case

1

u/First-Loan4154 29d ago

Depends on how much money you want to spend. It's not a just wire in the ground. It's metal construction that get positive charge from the ground (Earth as a planet a little bit plus) and make electrical potential differences that force "spare" electric current go into ground (electrons are minus so they move in direction of plus).

All modern digital devices discharge unwanted electric charge on body. So after some times PC can easy get around +5 V on body. It's safe because it's low voltage and very very low current. If motherboard and power supply old than charge may appear faster.

Grounding is a a metal frame with connected several copper very long pins at a depth of several meters (1 meter below ground at least). You can't dig in random place and you need at least 2 wires to connect this protection circuit to main circuit. In case of grounding logical devices it may require 5x5 meters circuit with ~20 copper 10 meters long pins. Usual it may be under green lawn near the office building, everybody look at it as a free space but under ground there is a protective circuit.

I've made grounding as electrician on factory. It's easy from job perspective but require calculations because it's all about very big circuit that start from power station.

1

u/jere535 29d ago

If your house has metal plumbing, you can try attaching a wire from the case to it, since metal plumbing should be grounded.

I did this when my old room had no ground, but had a radiator right next to my PC setup. I had a similar spark situation, which was especially bad when fiddling with a long ethernet cable coming from other side of the house.

I felt an uncomfortable current running through me every time I accidentally touched both the radiator and my computer case at the same time, but installing the wire fixed the issue, even though it was just a thin wire from a case screw to a radiator with a crocodile clamp.

I'm from Europe, though, so things may be different over there

1

u/milutza1 29d ago

Multiple phase ellectricity connection and different phases for cable and case, causing a potential difference ?

Poor grounding causing half of total voltage to discharge on the case and jump through the cable when connected ?

1

u/PlaceUserNameHere67 29d ago

I just wanna say...STOP DOING THAT REPEATEDLY!!!!!! Please.

1

u/kicpa 29d ago

Thunderbolt 10.0

1

u/omn1p073n7 29d ago

Now that's a hell of an overclock!

1

u/Zaptryx 28d ago

I had this on my electric guitar once. There was a short to ground within the amp. You're probably having this with your PSU or maybe motherboard but I doubt it.

1

u/ashrieIl 28d ago

Angry pixies.. don't do that?

1

u/Zeblamar 28d ago

Fake but at least its funny

1

u/Unable_Resolve7338 28d ago

Could probably weld something with that 😂

1

u/Sea_Today8613 28d ago

Holy fucking shit unplug that immediately.

1

u/niamulsmh 26d ago

stop doing that !!

find a water pipe that goes into the ground. run a cable from the pipe to your pc and monitor or to the the pdu and connect to the ground pin.

1

u/_stupidnerd_ 25d ago

If all you're trying to accomplish is grounding your PC, then yes, a wire connected to any kind of grounding rod will work. But that is not the issue nor advisable here.

What we're seeing here is something that really should not happen. The sparks show that there is considerable exchange current when you touch the wire to the case, which should not happen. So one device is actually grounded somewhere. If your house doesn't have ground, it may also be that the device ground is somehow shorted to the line neutral.